I am using a PMA KS 92-1 air temp controller. I go through the manual's procedure for entering parameters, but they will not change.
I have already RTFM, mostly, and contacted customer support (Danaher Controls USA).
Can anyone please help a new engineer out. :confused:
Yeah, I checked the internal switch ("Loc" switch) and it is properly set to run. Secondly, I have no idea about the password, this is a small part of an AEC extrusion system.
There is one parameter that I thought could be the culprit (ConF >> LOGI >> L_r) this parameter is to disable changing values from the front keypad. The current setting is 0 or disable (keypad setting enabled).
Also, I don't have access to a BlueControl adapter (whatever that may be), or a pinout of said adapter.
This should be very simple.šŸ™ƒ
http://www.pma-online.de/en/pdf/ba_ks90-1_92-1_e_9499-040-62911.pdf
close the switch and do a fact reset as described in chapter 11.
the software (bluecontrol ) can be downloaded from webiste, however you still need a cable with leveltransmitters(from serial to 5 volt), however basic things can be done from frontpanel.
SPF should be 0
L_R should be 1
watch after reset the the config is loaded into the para set.
if more just ask.
It worked!!!
Had to do a factory reset. Followed by a "FAC no". Values adjust and I'm in business.
Thanks shooter! (y)
Hi all, long time lurker and finally decided to sign on to get some help for those smarter and more experienced than I! I'll put it out there...
1,282
I recently had to work on some machines with PMA temperature controllers. These controllers required an RS232 to TTL converter cable which was...
21
17,722
I am interfacing KS800-DP modules (temperature controller made by PMA) with SIEMENS S7-317 2DP CPU, using PROFIBUS DP Communication. The GSD file...
3,145
Hello All, I've been tasked with automating a flatbed press that runs with some pretty extreme temperatures. I've been told it can run close to...
168