Point I/O communication through 1756-EN2T possible?

phuz

Member
Join Date
Jun 2008
Location
Mohnton, PA
Posts
1,044
We planned on our network using an EN2T in our controllogix rack to talk to all the Point I/O, but I get the dreaded yellow triangle on all the Point I/O devices including the 1734-AENT module. When I move it over to the 1756-ENBT module, everything works. Am I really prohibited from using the faster EN2T module?!? This doesn't make sense.
 
Should work but check that all your communication parameters are correct, that you have the project file's module matching the EN2T's version, stuff like that. Yellow triangle means you're almost there.
 
Highlight one of those 1734 modules and look at the error message at the bottom of the I/O tree or in the Connection tab.

You can definitely use POINT I/O with 1756-EN2T.

The most common issue I run into with POINT I/O is that the 1734-AENT adapter must be manually set to the correct Rack Size, using either RSLogix 5000 or the embedded Web page. Just configuring the -AENT size value in RSLogix isn't enough: you have to take an action to apply the correct adapter size.
 
LOL!
It helps if you don't fat-finger a subnet of 255.255.254.0 :)
problem solved. I was pulling my hair for an hour on this one.
Embarrassing, yes.
 

Similar Topics

Hi, I have some problem with View Point which I'm using to manual control of conveyors. On begin when in network was only PLC and HMI View Point...
Replies
0
Views
74
Hej guys i'm pretty new to communications between systems and i spent a while (arround 2 days) looking for similar stuff on the forums and since...
Replies
0
Views
2,895
I am using wonderware intouch 9.05 and 10.0 ver. suppose if i made a bottle filling plant in which a bottles are fastly moving and filled on...
Replies
0
Views
1,166
I have an issue with this 1734-aent, This has been an existing set-up. The 1734-AENT 192.168.1.2 card has been configured through Bootp with the...
Replies
10
Views
16,823
Hi, I want to test two mds4701A's communication. One connected to floboss103, another connected PC, Does anyone knows how to configure these two...
Replies
4
Views
7,930
Back
Top Bottom