Post subject: Mitsubishi PLC RS485 2W Communication to Weintek HMI..

Ray_Z

Member
Join Date
Dec 2014
Location
Lahore
Posts
5
We have two PLCs both are Mitsubishi-FX2N, and we want them to communicate to Weintek HMI MT8100ie.
MT8100ie can communicate with Multiple PLC and it Supports RS232 on Com1, RS485 (2W/4W) on COM1 and RS485 (2W only) on Com3.

So, we are using RS232 on COM1 for PLC1 and COM3 (RS485 2W) for PLC2.

PLC1 is successfully communicating over RS232 Com1 (after a RS422 to RS232 converter), but PLC2 is not. :oops:

What i have known Mitsubishi has RS422 default and its 4 wired. :whistle: Its our limitation we cant use 4w we are left with 2w mode.

We tried different Parameters and wiring but still we are unable to get anything.

Any help / Guidance in this regard will be highly appreciated.
 
With the Weintek you can only choose one port or the other. If you are using RS232 that is only for a single point communication between two devices. Not only that but RS232 requires 3 wire for read write communication. The Weintek can communicate with multiple PLC's But only in the RS485 mode where each PLC is addressable.
 

Similar Topics

I know it is fairly simple to post a screenshot, but many of us have large screens, so perhaps y'all could take the time to trim those screenshots...
Replies
4
Views
516
Good day all. Stupid question incoming (see my handle), but I can't seem to get this last step sorted. Basic story: Ops ruined the PC we were...
Replies
4
Views
743
We are experiencing VM OS corruption after Studio 5000 installation. This has occurred for several VMs. Strangely enough, not every VM is...
Replies
3
Views
1,410
Hi I’m struggling to understand how the LHTTP_post / get work ? I have a url address given to me by the IT , I have to send a works order...
Replies
2
Views
1,235
Hi, Just curious to how the job market is for controls engineers in the UK at the moment? I'm not seeing many jobs advertised, and wondering if...
Replies
9
Views
2,353
Back
Top Bottom