Power cable
ddeshi2
Dec 2010
Baton Rouge
89
Hi all, I would like to know how do ya'll determine the kind of electric cables ( wire guages) to be used for different applications. I'm working in a small company and the people here are trying to figure out the electrical cables to be used in an oil field. Does anybody have any idea??
The fact you are working in the oil field means that you
must use the national electrical code. section 500-5??
for requirements for installation. then look at table 310.16 for ampacity and table 310.15 for derating of the wire.
there is a lot more to what i have posted when doing electrical work and especially in hazardous areas like oil fields.
regards,
james
everything is run in sealtight with TMCX connectors. wire size depends on load.
the important thing is that gas can't travel up the conduit into the control rooms or explosion proof boxes. No sparks allowed. most of the area is NEC class 1 div2 with a few div 1 areas so read up on that in the NEC codebook
The short but maybe embarassing method is to ask your customer what he wants / needs. The embarrassing part may be when he says "youre supposed to know that stuff - what do I need you for?
To answer your question you need to know what the load demand is ie current, voltage
and if motor start current and max overload current,
lenth of wire run, how many conductors in cable or conduit, ampbient temperature,
environment stuff like dry or in wet weather, if in a combustible atmosphere (gas, liquids, combustible dust etc)
I cannot think of what else I am forgetting.
You need to get copy of a good electrician handbook and the NEC since you are in USA and start studying.
Dan Bentller
from my knoweldge...what ever voltage aboive 240vac are consider
power cable ...but each manufacturing have diffrent requirment..
feed mill,,gas mill, or oil have special requirment ..
u may follow ur national code for guideness
In the oilfield we mostly use CLX cable.The actual connector makes the box explosion proof or not. Readhead gland connectors on CLX is for explosion proof. Silverhead gland connectors on CLX is not. Most jobs i have done, were classified on prints as class 1 div 1 or div 2. Wire sizing depends on ampacity,deration factors, and other conditions. Shoot me an email([email protected]) with motor and amp spacifics, and i will try to help you in your search.
I need to send a signal to our PLC (Mitsubishi Q series) which is TRUE when there's current flowing and FALSE otherwise. The thing is, the cable...
31
10,165
Hi all, I'm trying to get a bom together for an R&D project. I have modbus devices that require 355mA for power plus communications. Does anyone...
1,319
A bit off topic, but I have an old heat trace controller where they used the power cable to get the rtd reading. They have lil pc board at the rtd...
2,015
I'm looking for if it even exist is a switch to open and close a micro USB cable for a Bluetooth antenna that can turned off via remote contact...
3,007
Whilst not a PLC question, I know that members here have a great diversity/depth of knowledge. One of my current projects is destined for the...
3,343