Dear,
I am computing a rough estimate on the power consumption for UPS for a PLC cabinet, the UPS will be also serving two flowmeters (each estimated at 15VA)
PLC cabinet consumption with the HMI will be around 600 watts
With reference to the attached, when adding the flowmeters should I consider the inrush current? 3A x 260 VAC? which will occur only for less than 5ms.
please advice
I would look at what the inrush will be with all of the other simultaneous loads during startup cycles of the system. Unless the manufacturer of the power supply provides for some sort of 'headroom' that power needs to come from somewhere when you are in battery mode. You will need to consider the inrush in your sizing. The HMI and PLC also have an inrush to consider, and of course the 125% 'engineering factor' we like to throw in for growth and general rear-end covering.
I was wondering if anyone had any insight on to how i could monitor and possibly graph Amp draw on our Powerflex 525 Drives. These drives are...
1,756
Hello, I want to ask about the power consumption of the 1769-Pb4: It is written that the input power consumption at maximum load is equal to...
1,816
Hi All, I'm having some trouble on determining the total power consumption of the following I/O modules: 1769-OB32,1769-OF8V, 1769- OW16...
2,640
Hello We have a 3 phase machine where we need to log the power use during every run of a process. Each run can last anywhere from 30min to 5...
2,289
Before I go into reading documentation for hours I would rather give you my scenario. I am looking to automate a home to the extreme and one...
3,042