power factor in hmi
rj061991
May 2014
iligan city
75
Hi! do you have an idea how to range powerfactor from 0 to 1 and goes back to 0 in a hmi.. it easy to range like 0 to 100 and display to hmi..but i found difficulties in power factor..from 0 which is capactve to 1 which is unity.. and goes back to 0 again inductive.. it like the range is 0 to 0.. using 0 to 20 mA?.
it seems range is both conficlt when programming in hmi.
its like this photo..how to display in hmi and calibrate?
search
Use positive/negative for leading/lagging?
That's exactly what we do, most devices that give you the pf in the first place will have a lag lead bit.
Some devices we see express it as a % of 100 too so -100% = 1 lagging and 100% = 1 leading.
OP, what device are you reading or using to measure the pf from ? Also your image link doesn't work......
i have on 0 to 20mA signal.. how to use it as negative/positive??... and is the range is still -100mvar to 100mvar??... im working on a project in a power plant..they have an existing analog reactive power meter.. what i want to do is transfer it to HMI that has a built it analog module..im using red lion crimson GMUIN4 module... it
You need to ask the people providing the analogue how its configured but logic would suggest that its -1 to 1 over the 0-20mA range
someone told me that i should use signal converter because the input signal of the old reactive power meter is -20mA to 20mA.. He told that i need to convert it to 4 to 20mA
So you have your answer then, and Rdast has told you in the other thread, if this is the same issue keep it all in the same thread,
Its getting mighty confusing
I am calculating power factor from samples of voltage and current. Calculation is done by multiplying voltage and current samples. What Im...
1,651
Hello, I was just curious if a PF correction capacitor is ever used with a VFD install? Have any of you ever needed to add a PF correction...
3,156
Folks, My boss say's he is paying a large fee due to Mostly inductive loads. He thinks it's because the guys come in and start up all the...
28
9,194
Hi gentelmen It is a pleasure to join you and discuss some information about hte PLC.Where i will graduate from the college this year and my...
1,758
Hi I'm trying to use the Cos function in the S7200 PLC, the answers I'm getting in the PLC don't match in anyway the answers I get from my trusty...
2,638