power flex 4m
vikas1947
Jun 2011
india
172
i have a drive of ab power flex 4m its input is single 220 v ac and output is 3 phase AC now i want to know can i give line and neutral of 220 volt ac directly to its input or i have to add some additional things what if i will give 220 volt input to it directly from the home supply....
I am not 100% sure of your question.
If I am right
and your household supply is 220 Vac
then that is the correct input for a single phase 220 V ac input
you should always have some form of protection ie Circuit Breaker and a contactor to be able to isolate power to the drive.
not for starting / stopping only for a power cutoff if needed.
EDIT: I just read where you said "home supply". You probably want an RFI/EMI filter to keep from sending noise to all your neighbors and the power company. I think some of those drives offer a built in filter. Check you part number against the manuals.
Yes, as long as you derate the drive at least 50% (due being single phase) and make your connections to R(L1) and S(L2) with no connection on T(L3) to ensure the cooling fan (if installed) and power supply are properly fed.
If you have low impedance supply or ungrounded power distribution then there are a couple more things to do.
re
now i connected my motor in star format with power flex 4m ,i gave input to motor through three phase wires and my motor is working but in motor body i found current that should be hazardous .i wasn't grounded the motor
we assumed you would know to do this - Very Sorry -
Normally the wiring to the motor is shielded (Screened) and Bonded to earth at one end, this stops noise.
On the drive the 'PE' terminal connects the Ground and to the motor earth.
Hope that makes sence
re
sorry wrong post ...so you tell me what i have to do now where i have to connect all the three inter connected terminals?
Your post #5 above is exactly how the drive and motor should be wired and grounded. You should also connect the two ground points, one on the motor and one on the drive, together with a bond wire so the grounds are at the same potential at all times.
Power flex 527 Network based safety drive had faulty and alarm pop up SOS Code internal fault Unable to set or clear the fault manually or...
136
Hi all. Would anyone happen to have the Modbus register datasheet for the Honeywell/EnergyICT EIMFlex Modular Meter v1.11 We've 40 of these that...
73
I have an issue with Power Flex 525 during running processing, the VFD stopped suddenly while the PLC and VFD connection ok, VFD does not have any...
138
I am trying motor startup with pf525 drive by using wizard start over ethernet communication but during direction test it's showing control error...
204
i have a flashing yellow sts light. "Stop Asserted" message on one of my PF 753"s, but no bits set in parameter 961. The safety circuit tests...
215