Hey folks. I created a routine in the power up handler folder in the controller in a 1769-L30ER. I wanted to have the controller go through a start sequence after a POWER LOSS. That is, controller has lost incoming power.
When I downloaded the program with that additional change plus others, the controller faulted, something to do with the power up routine. I cleared the fault and it runs fine.
Was this just because I DIDN'T lose power, so to speak, just did a download? In other words, is this normal?
The power up routine is it's own routine with it's own program tags. A-B said not to assign the routine in a task. There are, however, a couple of bits that are in the main task such as alarm reset and start.
Any help is always appreciated and thanks in advance. (I'm not sure how to include the logic on this post)
Been awhile but I think you need to clear the faults with the power up routine.
Pretty sure there’s a sample program in the samples folder showing how to do this.
From AB KB 22379
The power up handler in a Logix controller has one of two purposes. It can prevent the processor from returning to RUN mode if power has been lost and restored in run mode. It can also be used to run ladder in the power-up routine to take a specific power-up action. The routine must also specifically clear the power-up fault that is generated by having a power-up routine if a fault is not desired. On power-up, the following major fault will be generated if there is a power up routine defined and it does not clear the fault:
Type 01, Code 01, Power-up Fault, Power lost and restored in RUN mode.
If the fault is not desired, there are two options:
Remove the power up program
Handle the fault in the power up program as described in the common procedures manual
From AB KB 22379
OK Thanks. I'll look at that manual and see how to do that.
Thanks to all.
AB Sample power up routine code attached.
Note: To delete the Power-Up Handler Program, go to Controller Properties > Advanced and set the Power-Up Handler to <none>.
Example Ladder:
Download (Power_Up_Routine.zip) file and extract the Example Ladder (Power_Up_Routine.L5X)(see File Attachments below)
RSLogix 5000
Power-Up Handler
New Program... 'Power_Up_Program'
New Routine... 'Power_Up_Routine'
Import Rung... browse to the example file (Power_Up_Routine.L5X)
Perform Tests;
Cycle Power in Run Mode with code Inactive
Cycle Power in Run Mode with code Active
Observe differences
Example Ladder:
RSLogix 5000
Power-Up Handler
Perform Tests;
Observe differences
Thank you. I've found a lot of that in the common procedures manual. I'm almost ready to test it. Y'all have been a great help.
I have a controller issue I think. 1756-L63 Using RSL5000 v20.05 I can verify a project and download it, do online edits and monitor fine...
2,790
Hello, I'm new here and new to AB programming. I come from the land of DeltaV :) I have a CompactLogix 1769-L1, and found out how to...
1,410
Hello all, thanks for taking time to read this. I'm having an issue with testing the power-up handler and I cannot get a fault to occur. In the...
3,392
Hello. i have an AB Compactlogix with 2 racks of remote ethernet I/O at a station that suffers from occasional power outages. when the power comes...
3,269
237