PowerFlex 4 with 22XCOMM

grider75

Member
Join Date
Jul 2014
Location
Illinois
Posts
56
Does anyone know if its possible to pull amps or hz from this drive through the 22xcomm? I have it networked and added to my RS5000 configuration tree. I think you have to add more data links but not sure how or if its possible.
 
What network protocol are you using in conjunction with the 22-XCOMM-DC-BASE DSI External Communications Kit?
EtherNet/IP, ControlNet, DeviceNet, Profibus, BACNet, LonWorks?
 
Identical Topic:
http://www.plctalk.net/qanda/showthread.php?t=60889

Additional Thread:
http://www.plctalk.net/qanda/showthread.php?t=80807


Instructions:

p51, Chapter 6
http://literature.rockwellautomation.com/idc/groups/literature/documents/um/22comm-um004_-en-p.pdf

You will need both the Powerflex4 Manual and the 22-comm-e manual I linked above.
You will need to send a message to the drive asking for the parameter value where what you want to know is stored. Amps for example.
The parameter NUMBER where the Powerflex stores the AMPS value will be in the Powerflex4 manual. Parameter number structure can be different between drive models so always check that drives manual.
 
Last edited:
If you added the PF4 module to your RSL5K application without any "alterations" the Hz feedback from your drive will be found within Word 2 of your drive's Output data image(CPU Input) , decimal point implied.
Open up the Tag Browser, find the PF4 hardware defined tags, expand the I(Input) tag; the first word is referred to at bit level and represents the Status of the drive; Word 2 is examined at word level and it represents the drive's speed Feedback; for PF4 the feedback units are Hz(every other PF drive family returns EUs); if the Feedback shows 400, the drive is running at 40Hz.
I'd study the 22-COMM-E manual for the data transfer capabilities of the EIP comms adapter.

http://literature.rockwellautomation.com/idc/groups/literature/documents/um/22comm-um004_-en-p.pdf
 
Last edited:

Similar Topics

Hello, I am currently in the final week of my internship and I have encountered issues with communication between a PowerFlex 700 variable...
Replies
0
Views
53
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
Replies
3
Views
128
Hi, I'm currently having issued with a PowerFlex 252. It was working fine last week, and suddenly decided to stop working. When I go into...
Replies
2
Views
108
Hello, I'm hoping someone can help me with understanding how to set/change these data types. We recently swapped from Invertek to AB drives...
Replies
1
Views
100
All, I have a PowerFlex 525 driving an agitator motor. The goal is to have the agitator start automatically after a power loss or a comm loss. I...
Replies
2
Views
90
Back
Top Bottom