Good Evening ,

I’m trying to get our maintenance staff to set the IP Address for a 22-Comm-E
card for PowerFlex 40 drive . I usually use BootP , but is there a way you can use the built in HIM on a PowerFlex 40 to set the IP Address on the 22-Comm-E ? Shame on me if I overlooked this .

Thanks so much in advance
 
Thanks . I read that manual , but within the procedure with the HIM , it did not seem like it followed thru to the IP Address entry . I will try it tomorrow.

Thanks again ,
 
The HIM module is actually connected to a tiny serial "DSI" network with both the VFD control board and the 22-COMM-E.

Follow the steps on page 3-2 to switch from connecting to the Drive and its parameters, to connecting to the 22-COMM-E and its parameters.

The IP address itself is parameters 3,4,5,6 of the 22-COMM-E.

Be sure you enter a compatible Network Mask and Default Gateway, and disable BOOTP.
 

Similar Topics

Good Evening , What would be the best way to reverse a motor using a Powerflex 525 drive in RS Logix 5000 ? The drive is running in one...
Replies
1
Views
3,976
Good Afternoon , We still have a number of Powerflex 70 drives throughout the plant. Many are being controlled by DeviceNet that I plan on...
Replies
10
Views
6,686
We are going to start a new proyect which involve the use of 5 or 6 drives, an we want to know what is the best network for the powerflex drivers...
Replies
14
Views
5,050
All, I have a PowerFlex 525 driving an agitator motor. The goal is to have the agitator start automatically after a power loss or a comm loss. I...
Replies
2
Views
33
I've got a Powerflex 700 that doesn't like to get going in the mornings. This motor will run anywhere from 30 seconds to 5 minutes before it just...
Replies
3
Views
173
Back
Top Bottom