Powerflex 525 PID Controll for a Pump in a Hot Water Set

You probably want a small deadband around your pressure setpoint as well. Assuming it isn't critical to be right on the money.
 
+1 on the deadband, there is a parameter for that. Also, think about failure mode. If the pressure sensor fails, and thr drive sees 0mA on the input, do you want the VFD to go full speed or to stop? If you want it to stop, you may want to invert the control action, and also invert the pressure transmitter signal (many IFMs can do that). Otherwise there is a parameter in the drive to disable itself if the analog input falls below an adjustable level.
 
+1 on the deadband, there is a parameter for that. Also, think about failure mode. If the pressure sensor fails, and thr drive sees 0mA on the input, do you want the VFD to go full speed or to stop? If you want it to stop, you may want to invert the control action, and also invert the pressure transmitter signal (many IFMs can do that). Otherwise there is a parameter in the drive to disable itself if the analog input falls below an adjustable level.

Any idea off hand what that parameter is to disable itself if the input falls below? Other than that I have it all good to go just was wanting to have that ability for if the IFM dies.
 

Similar Topics

Hi all, Small panel built with a micrologix 1000 and a 525 drive. The micro is simply for start/stop/control of power flex and some lights and...
Replies
5
Views
2,151
Hello, I take part in commissioning of process station with lobe pump. Speed of the pump is controlled by PowerFlex 525. A customer requirement...
Replies
7
Views
5,567
Fairly new to the drive so apologise for the layman terms. Textile machine uses PF525 VFDs to control motors. The speed of the drive is currently...
Replies
5
Views
90
Hello, I'm hoping someone can help me with understanding how to set/change these data types. We recently swapped from Invertek to AB drives...
Replies
1
Views
117
All, I have a PowerFlex 525 driving an agitator motor. The goal is to have the agitator start automatically after a power loss or a comm loss. I...
Replies
2
Views
107
Back
Top Bottom