forqnc
Lifetime Supporting Member
Hi All,
I am working on testing a project with a Powerflex 525, final project will be a 755, and I am trying to reset the Elapsed kWh meter over Ethernet.
I thought I would be able to add the parameter ResetMeters (A555) into Studio 5000, then move a 1 into the parameter then back to 0 but this does not work.
I also tried to enter a 1 into the controller tag, still does not work.
I see A555 change briefly to a 1 then back to 0 on the drive, but it is not resetting the meter.
If I changed A555 to 1 using the drive keypad it works.
When I do this using a Yasakawa drive, I set H5-11 to 1 so I do not need to send an Enter command when I change a parameter, does the Powerflex 525 have something like this?
Any assistance is appreciated.