PowerFlex 525 - Using Step Logic within Drive can you change direction ?
Aug 2016
Virginia
343
Good Afternoon ,
I have a project that I am beginning , that I will be using 3) PowerFlex 525's
drives. I took notice of the StepLogic feature in it. Is there a way you can change the direction of the motor using the StepLogic feature ? I would like to tell the drive to start , go to a limit switch ( Drive Input ) , stop and go back to a home limit switch , then activate a drive output telling that the cycle is complete .
Thanks in advance ,
If you check out the bottom of page 206 of the manual for a Powerflex 525 I think you will find that you can do exactly what you are talking about by using the auto homing function of the VFD with your limit switch(s). And you can get your feedback from the enhanced control word it seems.
After replacing the 70 with the 525, the PLC can read from the drive and recognizes it as online, but no commands are being listened to. PLC is...
565
Good Morning , I would like to start a Powerflex 525 with a N.O. Start Pushbutton , and when the N.O. Start Pushbutton is released I would...
1,674
Hi, I have a potentiometer connected to a siemens micromaster 440 to control a servo motor speed and they are not connected to any PLC. Now, I am...
4,049
Good Morning , I have a quick question about the Powerflex 525 embedded ethernet drive. I'm using a CompactLogix 1769-L18 and using Ethernet...
1,764
Good Morning , I'm building a control panel with PowerFlex 525 drives. I have black wire for the 480 vac , red for 110 vac , blue for 24 vdc...
2,905