Powerflex 527 CiP drive and Safety Signature
PiperJohn
Mar 2022
Michigan
61
I swapped out a PF 527 drive that has been giving me occasional faults.
I replaced with a new 527, assigned its IP and gateway and cycled power.
When it powered up I could go online with controller via Studio5000 but had an I/O fault (blinking green light) and lost communication to all the drives. They all had the little yellow exclamation mark next to them.
I recall that this has something to do with the safety signature not being assigned to the new drive.
Problem is I can't connect to any module in order to change it.
Anyone care to shed some light on the procedure of how to reset this mod fault?
I ended up just putting the bad drive back in until I figure this out.
Search 520-UM002C-EN-E for the PF-527 manual. Chapter 3 should have all the info you need. Could be a power structure mismatch, or need to set compatible module for electronic keying.
Thanks I'll take a look.
It's a 5380 safety controller so I thought it was it wasn't seeing the safety signature in the new drive.
To answer my own question;
Yes, I/O fault was caused by Safety network number.
Right click drive replaced to open module, click box with dots (...) under general tab, then click set. Yes, to accept. Then cycle power to the drive.
Hi all, I am having issues with a Powerflex 527 STO. I am hard wiring a safety relay (guard master MSR27TP) to S1 and S2 and also the common to...
1,806
I am trying to setup the new powerflex 527 to use for training purposes but it wouldn’t let me to finish adding it to an IO and I would get an...
1,199
I've got motor that ran fine for years, but now it's sarting to overshoot its target position a few times a day. Is this indicative of a motor...
24
5,763
Sorry its probably a stupid question. I have version 1.008 PF527 which going to be replaced with a FW Version 2.001 Unit. I have version 32 logix...
1,496
Hello, Currently trying to replace a powerflex 527 drive in a machine for motor rotation. The drive is wired the same way and it is the exact...
3,453