Powerflex 527 STO Safe Torque-Off hardwire
macrolegend
Jun 2019
Hamilton
Hi all,
I am having issues with a Powerflex 527 STO. I am hard wiring a safety relay (guard master MSR27TP) to S1 and S2 and also the common to 01 as per the manual. I also set up the Powerflex configuration connection to "motion only."
I am still getting an fault/error on the powerflex saying "INHIBIT M05 – SAFE TORQUE OFF." Is there something I am missing that I didn't wire up correctly or a configuration parameter I forget to enable/disable? Any help would be appreciated.
Are you using the source voltage S+ terminal from the drive into your S1 and S2 inputs via the safety relay? Or are you providing an external 24v signal to S1 and S2 through the safety relay? I'm pretty sure these are tested outputs so S1 and S2 have to have the signal from S+ terminal on the drive.
I haven't used the 527, but have done a number of STO applications on 525s. You can use an OSSD signal or just straight 24V as long as the 24V source shares a common. The OP's point about connecting common to terminal 01 implies that they're using an external 24V supply.
Double check the voltage on S1 and S2, like DarrylR suggested. You may also need a fault reset signal once the STO is re-energized. In the 525, there's a parameter that enables/disables the STO fault. By default, it faults the drive when STO is removed. If the parameter is changed, it doesn't fault the drive, basically making it an "auto reset" safety function.
I measured voltage at S1 and S2 and I am getting 24v, and yes you are correct I'm using an external 24V power supply. I believe I might have found my issue. These drives were previously used on another system that used safety over ethernet, I found that you could have these weird inhibit faults on the drive and the only way to clear them is to factory reset the drives and to do that you reset the safety ownership. I am currently trying to do this and will get back to you guys if this the fix. This is the article I found on Rockwell website that might potentially fix my issue: https://rockwellautomation.custhelp...fety---reset-to-out-of-the-box-configuration-
Just wanted to update everybody and that resetting the ownership to all the VFDs that were faulted via the article knowledge base that Rockwell provided cleared the fault/issue. If you happen to use a powerflex 527 using safety over ethernet then have to switch over to hardwire please make sure to reset the ownership and keep the module inhibited until you have switched the connection to motion only
I am trying to setup the new powerflex 527 to use for training purposes but it wouldn’t let me to finish adding it to an IO and I would get an...
1,199
I swapped out a PF 527 drive that has been giving me occasional faults. I replaced with a new 527, assigned its IP and gateway and cycled power...
2,032
I've got motor that ran fine for years, but now it's sarting to overshoot its target position a few times a day. Is this indicative of a motor...
24
5,759
Sorry its probably a stupid question. I have version 1.008 PF527 which going to be replaced with a FW Version 2.001 Unit. I have version 32 logix...
1,496
Hello, Currently trying to replace a powerflex 527 drive in a machine for motor rotation. The drive is wired the same way and it is the exact...
3,451