Powerflex 70 Copycat Usage

jamesau

Lifetime Supporting Member
Join Date
Mar 2004
Posts
181
Some guidance here would be appreciated.

I'm commissioning a system that has several drives installed and configured. One of the motors/drives needs to be uprated to match an existing one. The new unconfigured drive has been installed and I'd like to have it configured to match the existing one. The manuals refer to the copycat feature and this reads like the easy way to go.

I'm a little stuck on the procedure for using copycat. Do I do a HIM Copycat (device -> HIM) on the existing drive, take the cover/HIM off that and place it on the new one and do a HIM Copy (HIM -> device) on the new one? Is there more to it than that? The manuals/knowledgebase aren't clear to me on the procedure.

(I didn't specify or configure the drives; those that did are gone and I'm kinda new to these).

Thanks in advance for your help
 
It has been a couple of years since I did it last but I do think you are correct and it was that easy.

Hope this helps.
 
Yes, that's the basic procedure.

It's not a perfect process; if your drives are very different (like PowerFlex 700 Series A versus Series B, or PowerFlex 70 versus 70EC) then the HIM Copycat won't work. There was also a bug in version 4.003 of the PowerFlex 700 Series B firmware that made Copycat not work correctly.

But for basic PowerFlex 70 -> PowerFlex 70 copying, it's generally pretty simple. You copy the active User Set of parameters into the HIM Set, then move the device and copy the HIM Set into the active User Set.

Remember that the configuration of a communications module like the 20-COMM-D or 20-COMM-E is independent of the parameter set of the drive. You can use the Copycat for that, too, but you need to specify that you're copying the DPI module parameters, not the drive parameters. I prefer to do the communication module configuration by hand.
 

Similar Topics

Good Morning , Had a PowerFlex 70 go bad . Uploaded the parameters to the HIM . Did not have the right drive replacement . The HIM says...
Replies
1
Views
1,803
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
Replies
2
Views
55
Hi, I'm currently having issued with a PowerFlex 252. It was working fine last week, and suddenly decided to stop working. When I go into...
Replies
2
Views
84
Hello, I'm hoping someone can help me with understanding how to set/change these data types. We recently swapped from Invertek to AB drives...
Replies
1
Views
88
All, I have a PowerFlex 525 driving an agitator motor. The goal is to have the agitator start automatically after a power loss or a comm loss. I...
Replies
2
Views
86
Back
Top Bottom