Hello all, I am currently having an issue where the plant want's to decrease transfer cycle between roll beds.
I was able to achieve this by increasing the Preset Spd 1 (param 93 in this instance) from 65hz to 72hz. To achieve this I had to open drive executive and change that parameter manually. Increasing through the PLC wasn't registerting in the PowerFlex. I can control the speed through the PLC from 65hz all the way down to 1hz but increase it just to 66hz and it won't take.
FYI
Param 82 max speed = 75hz
Param 83 over speed = 10hz
If anyone has experience anything like this, any help would be appreciated.
I was able to achieve this by increasing the Preset Spd 1 (param 93 in this instance) from 65hz to 72hz. To achieve this I had to open drive executive and change that parameter manually. Increasing through the PLC wasn't registerting in the PowerFlex. I can control the speed through the PLC from 65hz all the way down to 1hz but increase it just to 66hz and it won't take.
FYI
Param 82 max speed = 75hz
Param 83 over speed = 10hz
If anyone has experience anything like this, any help would be appreciated.