PowerFlex 70 Stop Assertd issue
mgostovich
Aug 2022
Yakima,WA
We are running a power flex 70 connected to a Delta V and I cannot get the drive to start because I am getting a STOP ASSERTD message on my HMI. I cannot start it manually or through the Delta V.
Any Answers or thoughts???
Welcome to the PLCTalk forum community !
Is the connection hardwired, or over a network like DeviceNet or EtherNet/IP ?
Usually the Stop Asserted message means exactly what it says: something is holding a STOP signal true.
One common one is the digital inputs: DI1 is by default a STOP signal that has to be wired True to remove the STOP command.
That's inverse from the STOP bits in a network command. DI1=TRUE means "do not stop", while Bit 0 of the command word = TRUE means "stop".
There's a parameter that tells you which DPI adapter (onboard inputs, network, etc) is issuing the stop command; I know it's called "Stop Owner" but I don't have a PF70 manual at my fingertips to tell you which parameter number it is. I think there's an "owners" section of the parameter list to tell you which part of the drive's control structure is issuing starts and stops and reference commands.
It is hard-wired in a classroom setting. I even tried removing the DI's one at a time and restarting it but nothing changed. When I loop at the DI settings, DI1 is set as "STOP-CF". should I change that to "not used"?
Thanks for the help
Hey all, I am currently working on a depalletizer for a customer and we are doing a hoist upgrade. This is a SLC500 processor and the drives are...
297
We are an OEM of reinforcing fiber dispensing machines for asphalt production. I am experiencing an intermittent issue with several machines...
886
Hi everyone: Is there a way to stop a PowerFlex 755 in a fast ramp and then hold the motor for a few seconds? I need this to avoid the load to...
1,267
Good Morning , I would like to start a Powerflex 525 with a N.O. Start Pushbutton , and when the N.O. Start Pushbutton is released I would...
1,669
Hi all. Having a problem with a PF 525 TermBlk 5 input. I came across the drive the other day and not sure how its running. Both the Enable...
2,143