PowerFlex 755 stop and hold

VulcPAC

Member
Join Date
Oct 2018
Location
Mallorca
Posts
21
Hi everyone:

Is there a way to stop a PowerFlex 755 in a fast ramp and then hold the motor for a few seconds? I need this to avoid the load to rotate with the inercia after the inverter releases the motor.
I tried "Ramp to Hold" but I cannot control a delay time, it remains with the VFD active and 0 speed until the next start. For now, I dont have wire stop to Di to use as a "stop mode B", only a stop command via Ehtenet/ip.

The other question, in case that I need a very fast stop, if I use "Current limit Stop", do I neccesary need a dynamic brake resistor? Can I use "current limit stop" and bus regulator with "Adjust freq"? Is a powerflex 755, 400V, 2,2 kw, motor with gear box and a unwind roll as the load. For now, I dont have the data of weight and inertia, is not a huge mass, I am just controlling the torque or speed with a diameter sensor with an equation in Logix.

Thanks!
 
I found this in the reference manual:

Ramp mode can also include a timed hold brake. Once the drive has reached zero output hertz on a Ramp-to-Stop and both parameters 395 [DC Brake Time] and P394 [DC Brake Level] are not zero, the drive applies DC to the motor producing current at the DC Brake Level for the DC Brake Time:

But my doubt is if I can use DC to brake withot having a braking resistor.

Thanks
 
The DC hold injects DC into the motor windings, so best not to use it for long periods as it can cause motor winding temperature rise.
The braking resistor is used to limit the DC bus voltage during rapid stops as the motor will act as a generator putting energy back into the VSD, the brake resistor is turned on to shunt some of this energy into the resistor when the DC bus goes over a certain value.
 
The DC hold injects DC into the motor windings, so best not to use it for long periods as it can cause motor winding temperature rise.
.

Hi. What do you mean with "long periods of time"? For example, in a 2,2 kw VFD, inject DC with the default value of 8.7 Amps diring 3 seconds after the stop, could be considered a long period of time?

Thanks
 
Maybe I'm not seeing the whole picture but if you have EthernetIP...
1. You can set the Accel Rate as a datalink which will allow the program to set a rapid decel when desired or a softer decel when not desired.
2. When you want to stop fast, change the speed setpoint to 0.0 and the accel rate to a fast decel. The drive will decel fast to zero speed and hold it there.
3. After the drive has held at zero speed for the desired time, then issue the stop command.
 

Similar Topics

Hi guys, We have PF 755 induction Flux vector control. When the drive stops the current doesn't drop to zero. It stays for 20 seconds. What...
Replies
6
Views
2,720
Quick question? What is the difference between START and RUN links when controlling Powerflex755 through Ethernet/IP?
Replies
3
Views
4,910
So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
Replies
9
Views
273
Hi I was wondering I need to update the firmware of a 755 inverter does the drive hold the program on the drive and just updates the firmware or...
Replies
5
Views
172
So I'm replacing a terminal block on the inverter board for a 755. I'm wondering if anyone knows what conformal coating would be best? I'm not...
Replies
1
Views
139
Back
Top Bottom