PowerFlex 700 Problem....

JoseM

Member
Join Date
Jul 2011
Location
Texas
Posts
381
Can anybody give me some guidance on how to troubleshoot a PowerFlex 700 drive.

I have this VFD drive driving a pump that doesn't want to run. I checked that the code on the "ControlLogix" is sending the command to start to the VFD. I also talked to AB technical support and they told me that communication should be working correctly.
 
How is the drive controlled? What does the display on the drive say? Have you looked at what the digital input status parameter is telling you? Do you have a hardware enable on the drive?
 
I just discover that various parameters where change under the "Communications" mode of the PF700. Parameters like "Logic Mask", "Start Mask", "Direction Mask", "Reference Mask", etc. They where set to [000010] and the correct setting according to Allen Bradley technical support is [111111].
 

Similar Topics

We are using Powerflex 700 VFD to drive the starting motor of gas turbine. Reference speed signal to VFD comes from AB control logic PLC. When we...
Replies
6
Views
3,506
Hi Everyone, I had to replace PowerFlex 700 20BC085A0ANNANA0 with this one 20BC085A0ANNANC0. I set all (I think all) parameters the way they...
Replies
9
Views
4,126
This is about the third PowerFlex 700 drive I've put in and I've had the same issue each time getting it to run. In this case it was wired for...
Replies
4
Views
5,240
Hello, I am currently in the final week of my internship and I have encountered issues with communication between a PowerFlex 700 variable...
Replies
0
Views
58
I've got a Powerflex 700 that doesn't like to get going in the mornings. This motor will run anywhere from 30 seconds to 5 minutes before it just...
Replies
3
Views
199
Back
Top Bottom