Hello, I just replaced a blown PowerFlex 755 drive. I set the IP address from the HIM to the correct network address. The drives has no faults, but I do not get the correct System Value at the PLC. I can connect to the drive with CCW at its network address. I have attached a screen shot of the communications test in the PLC programming. Could this be a function of an incorrect subnet or gateway?Capture.PNG
There are a few jumpers on 755, did you mirror those onto the new drive?
Do you see it on RSlinx at same address as the old drive?
What do the indications on the front of drive show?
Did you have a backup 755 parameter file from old drive? (there are a ton of parameters on a 755.
The builder supplied me with the parameters at commissioning and I used CCW to write them to the drive. I do see the drive connected in RSLogix "Who active" at the configured IP address. I see the drive in RSLinx as well. The IP address and subnet I entered at the HIM on the drive. I entered no gateway so this should be at the default value. I do believe that the jumpers are correct. My Status LED is flashing green, and my ENET LED is flashing green. This drive controls a small conveyor. When I force the conveyor on from RSLogix I get no run command at the drive.
download this pdf shows status of lights and whats wrong.
Rockwell Automation Publication 750-PM001E-EN-P
flashing green for both i think is NOT good comms. MISPOKE
STS flashing green = drive ready but not running, and no faults are present.
ENET flashing green = adapter is properly connected but not communicating with any devices on the network.
LINK flashing green = adaptor is properly connected and transmitting data packets on network.
HIM module display will tell you the issue.
Usual suspect is the drive is not enabled by estop.
when you force the conveyor to on thru plc does the HIM display run?
If it does display run, what does the Hz display below it?
Hello, I just replaced a blown PowerFlex 755 drive. I set the IP address from the HIM to the correct network address. The drives has no faults, but I do not get the correct System Value at the PLC. I can connect to the drive with CCW at its network address. I have attached a screen shot of the communications test in the PLC programming. Could this be a function of an incorrect subnet or gateway?View attachment 60553
That GSV is telling you that the drive is in a faulted state.
Check your firmware revision. If you had say a version 10 on the original, and you put in a version 14, you will need to match the revision before the project will take it again. If your running version 30 or greater in studio simply go offiline, connect to the drive and do a "match Drive" version 30 and below, if your on Version 31 or greater, use the "Sychronize" button. After that do a download to PLC and it should take it. This is very simple to do if this is the problem. Curious to hear the outcome
You hit the nail on the head
I apollogize. I should have updated this thread sooner. It was exactly that, a firmware revision conflict. I was working from CCW at the onset, but eventually went online with RSLogix and found the discrepancy. I was able to "match" the revision, and my communications error went away.
So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
271
Hi I was wondering I need to update the firmware of a 755 inverter does the drive hold the program on the drive and just updates the firmware or...
172
So I'm replacing a terminal block on the inverter board for a 755. I'm wondering if anyone knows what conformal coating would be best? I'm not...
138
Powerflex 755, running 2 weeks, and faulting with code 17 input phase loss.
228
Hi All, This is my first PowerFlex 755 drive setup and I am having an issue with when I start the drive it runs at my minimum speed 5Hz, but...
432