PowerFlex Multi Drive Issues

DamianInRochester

Lifetime Supporting Member
Join Date
Jan 2011
Location
Rochester NY
Posts
1,292
System:

1769-L23E Processor
PF40 mounted with an 20CommE
qty 4 PF4s daisy chained RS485 to PF40

I keep getting an F071 which is called "Net Loss"
This seems to point to the Enet comms as opposed to the RS485 commms.

On the Connections TAB is simply says status "Running" and doesn't even indicate a fault.



Another very odd issue.
If I click on the drive tab and then click "Connect to Drive" it goes through the correlation. But it always says there are differences between the project and the drives. If I download and save, Upload and save, not matter what when I go to correlate again it claims there are differences. I don't see anywhere where these supposed differences are listed.

This is about the fifth in line of a nearly identical system and this is the only with this issue.
 
The comms fault appears to have been a faulty ethernet cable. I suspect the shield was terminated on both ends and was creating a ground loop.

The "correlation" issue still bugs me. Every time I connect it claims that there are differences between the project parameters and the drive parameters. When I choose "details" and compare them one at a time, a message pops up stating that NO differences were found. Seems to be a bit of a bug.
 

Similar Topics

I had to replace 3 PowerFlex 40 multi-drives that each had 3 PF4M daisy chained off the DSI port. The PF40s had comm-e cards installed for...
Replies
9
Views
2,449
I have a machine with a CompactLogix ver20 and PowerFlex 40 multi drive node. That PF40 has a Comm-E ethernet adapter and has four PowerFlex-4Ms...
Replies
0
Views
1,893
Hi All, Tearing my hair out! I have had this working in the past but cannot figure out what is wrong now! Simple set up. PF 525 set up as...
Replies
1
Views
4,133
I have a problem with 2 powerflex 40 connected via 22-comm-E (multi-drive) with a compactLogix L32 controller. I'm sure I've correctly set all...
Replies
1
Views
4,499
I am attempting to perform a "scattered" read of parameters on a Multi-drive setup of 1 PF40 and 4 PF4 drives over EIP from an L23E. The 22-COMM...
Replies
2
Views
2,130
Back
Top Bottom