:mad: I have a PowerFlex70 5HP VFD and want to hook up the digital inputs as Sink inputs. The User Manual states that you can use Sink or Source but does not show Sink Hook up. The Powerflex40 has a switch to change between Sink/Source but I cannot not find any swith or jumper for the PowerFlex70!

Does anyone know how to set the powerFlex70 up for sink inputs?

Thanks
 
1. It is better to post in the main forum than in the practice area. You get more views.

2. It depends on what is hooked to terminal 8 (Digital In Common). If DC common is hooked to terminal 8 then +24VDC is to be switched to the inputs. If +24VDC is hooked to terminal 8 then its DC common must be switched to the inputs. You could use the on board source of 24VDC (terminals 7 and 9) or an external supply.
 

Similar Topics

I have an issue with a Powerflex70 drive communicating with a PLC5. The drive is setup as 1/2 rack and is communicating over remote I/O. It is...
Replies
6
Views
1,823
Hey folks. Quick question about direction control on a PF70. The control is all over the connection on the 20-COMM-E. Start, Stop, Speed...
Replies
5
Views
2,114
I need to add a couple of older PF70 drives to an application using PlantPAX, the 750 series have a fault list code in the library, but not the...
Replies
4
Views
1,619
Hi, We have a Allen Bradley, Powerflex70 series A drive. We would like to use it as a test bench and programming station for communication...
Replies
3
Views
1,589
hi we have a controlNet network with a PLC 5555 and several PowerFlex70 that are networked via COM C network adapters. Recently one of the...
Replies
2
Views
1,260
Back
Top Bottom