hI would like to thank you all for giving me your expert advice.
I have been out all day taking care of electrical field inspections so I apologize to everyone for not being able to reply sooner.
ArikBY
"The result came from your reference. it much esay to let the VFD to do the PID loop."
---I wish it was this easy Arik, unfortunately there are differentmodes of operation that require digital reference speeds and different modes that require PID control. My mistake for not mentioning this at the beginning of the thread, sorry about that.
Kevinrcase
"I hope that the input can be filtered either in the drive or transmitter since the static pressure would not be as tame as lets say level in a tank control loops."
---You are absolutely correct on this Kevin, in my particular setup (mechanically), there are fluctuations in pressure and this sometimes causes problems ie. the VSD continuously hunts for the optimal speed to run at. Filtering can be used in the PLC and also sampling time can be played with to address this problem.
DickDV
---That is correct Dick, the pressure is to be ambient at atmospheric or a bit +/- depending on the user.
"...you will need a sensor/transmitter that sends 4ma somewhere at negative pressure and 20ma somewhere at positive pressure."
---The transmitter that is installed is a differential pressure transmitter, the low side is connected to ambient, and the high side is connected to the cabin. I have read the values obtained from the P.T when the unit is off, we get a value, if the unit is running negative, we get a value less than ambient (when it is off), and the opposite when the unit is positive. Wouldn't this just be a matter of scaling these values? Once they have been digitized in the PLC, we can interpret the values any way we like. There is an HMI operator interface being used to change temperature and mode of operation.
Kevinrcase
---That is indeed correct, the scale will be in W.C.
DickDV
"As I think further about this, the drives I'm most familiar with do have the software option of setting up the input for 0ma to 20ma."
---That is a wonderful idea, never thought about doing this before. The PLC analog card has dip switches that I can change from either 4-20 or 0-20mA ranges. Great idea!
DavidFurut
---The fan is a reversed incline fanwheel and there are some pulsations in the pressure. The pulsations can be filtered out in the PLC.
Tom Jenkins
That is a very good point about the maintenance doors being opened. Fortunately, I have installed some limit switches on the doors that can react to the doors being opened, ie. hold the running speed until the doors are closed. The setpoint with dead band control sounds like the solution to the problem. I will check out Foxboro, Invensys and Rosemont to see what they have.
Thank you all for your great responses and your professional expertise, I think I have an idea of how to tackle this problem now and sounds like the setpoint with deadband control will be the solution.
TamHo