I am newbie in S7. In our plant S7-414H PLC with WinCC HMI are used. One of Pressure Transmitter reading is momentarily off in WinCC and then again ON. It is happening several times in a day. We checked in the transmitter signal is ok, power supply is ok and there is no hardware fault in CPU and analogue module. Is it communication problem? Could any body tell me how to check? WinCC PC(version 6) is connected Through CP5611 card with MPI of S7-414H PLC.
Hello arocon;Before you check on the WinCC side, I would look at the status of the analog signal in the S7-400.
Usually there is a scaling block used to set the engineering units on an anlog value from the field. Trace the PIWxxx value for the transmitter, see if the value is stable (try a VAT table for example), then follow it to the scaling block. Check whether the signal is stable at the entrance and the exit of the blocks.
If the signal is stable in the PLC, I would look in the Tag Management (in WinCC) for this transmitter value. If you are online in Tag Management, and you go down to the transmitter tag, placing the mouse cursor on the tag name will bring up a tooltip with status data on the connection. A "bad" conection will indicate communication problems between the PLC and the WinCC, possibly in the driver.
Come bac to us when you have more details.
Hope this helps,
Daniel Chartier
"Momentarily off" how? Incorrect value?
Are you scaling the value in the PLC? Are you assigning a value in the plc to it's register once ? Using multiple assigns to a variable in a PLC when scaling is sort of common, but HMI's don't scan synchronously to the PLC, and can occasionally get one of the intermediate values.
Does anyone have experience wiring this type of analog pressure transmitter up? It's 4 wires. 3 blacks and 1 green which I assume is earth...
290
I need to protect some pressure transmitters from hot (120°C) oil. Does anyone have a favorite transmitter cooling element/standoff they use...
177
Hi All, Just wondering what the best/most accepted way to measure tank level off pressure transmitter. Pressure transmitter is located in line...
1,944
I'm trying to wire a Endress+Hauser PMP71 Pressure Transmitter to a Schneider Electric TM3AI2H Analog Input Module. The Pressure Transmitter is...
1,317
Hi folks, I am having a hell of a time getting an E+H PMP23 scaled correctly in a CompactLogix PLC. I have tried all sorts of data manipulation...
19
7,071