Problem v17 to 24 logix5000 conversion
Jun 2017
Manila
Good Day Sirs!
I'm now having problem on a system that runs formerly in version 17. I upgraded it to version 24. I simply Upload the program then change the version and then downloaded it to the new v24 processor. I'm Having issue in the analog input modules because of its wrong reading, it has now an offset during its Low Signal. What am I missing here? Thank You for those who will response.
Ralph
Hi max.
The module settings of high and low engineering is defined in the configuration tab in the module. No other logic control these parameters.
I think i see the problem. There is a minor fault. Chxx.calfault is set to 1. Is it normal when you change to a new cpu, the calibration settings should be calibrated again?
Thankyou for your reply guys.
I was working on a new system upgrade where we were replacing a TI PLC with AB PLC. Other parts of the system had AB PLC (ControlLogix L61) with...
3,870
Hi everybody, We have a Powerflex700S Phase2 Drive in use. To set this Drive up I used the Startup Wizzard from Drive Executive (Autotune etc.)...
2,623
On all pages of my project i have a lot of information, texts and details that should not not be shown. I can remove them for each part apart from...
40
Hi, I have had problem with upgrading some projects from v16 to v18. I tried it on 3 diffrent computers. I want to post this so that anyone that...
176
Hi, I am having a challenge installing a new drive ACS355-03E-44A0-4 as it keeps on displaying Fault code F00018 even when the load is not...
135