Problem with 1756-IF16 AI Module
shamyl
Sep 2007
Pakistan
21
Last week I faced a problem with a 1756-IF16 analog input module. All the channels being used started showing 15-20% greater values than expected. e.g. two values which should have been zero were around 1000 and varying. I checked the mA at the input (all channels are configured on 0-20 mA and scaled on 4-20 mA). The actual mA on both channels were zero. I changed the IF16 module but the problem persisted. I reset the module using the RSLogix configuration and all values returned to normal. Within a week the problem has appeared again, but this time even the 'Reset module" is not working. The values which should be zero are varying between 50 & 1000 (around 1-20% error) , while the actual mA on the channel are constant at 4mA.
The module is showing a minor channel fault, but that's because of a couple of un-connected channels configured on 0-20 mA. Can it have anything to do with the problem? If not, what might be causing the problem? And what is the solution?
Double-check your channels are wired as per the samples shown in the manual.
I believe the terminals marked RTN must be tied to input RTNs, but don't know the details.
What is the data format set to? I had the same thing happen and Daba is right on by saying to make sure the "rtn" is connected. I had one channel with a bad connection on the jumper and caused problems on all channels
Dear Colleagues, Now I'm testing Rockwell-based control system that has been stored for 8 years. Have some major issue, that have not met before...
1,194
Good evening, just a dump question, I’ve configured channel no 13 with scalling as attached, then shown not linear reading, even when i simulate...
1,713
Hello All. We have a 1756-17 slot chassis with analog ins and outs in the entire rack along with the EN2T card. Up until recently everything was...
1,497
Hi guys, So I added a routine in a L71, and as is my nature, I selected all of the rungs and pasted them into Notepad++ and then re-imported them...
3,722
Looking for anyone with experience on these modules. I had a strange problem this morning and I'm looking for an explanation and so far I can't...
1,737