Hello,
I still have new problems with the migration of Panelview 1200
to Panelview 1500 Plus using Remote I/O on the PLC5.
Now I get the errors:
PKTX RIO Adapter Driver detected Block Transfer size mismatch for
BT7 Rack 2 Slot 0 driver, BT8 Rack 2 Slot 4 driver, BT9 Rack 2
Slot 8 driver.
I have attached the converted BT configuration (RSView Blocks.zip) and the Block Transfer in the PLC5 (Transfer Blocks.zip).
Who can help me to fix this?
mulderm
mulderm said:
Hello,
Slot 8 driver.
mulderm
Looking at you screen captures,
It appears you have the block sizes set to 32 bytes in your PV+ application. The BTW in the screen captures indicate sizes of 8 , 7 and 8. I have not done RIO on PV+, but I do know from other applications, block sizes must match
Ian
But I get the error messages!
When I set the sizes from 32 to 8,7 and 8 the module
groups/slots are different.
What is the solution for this?
mulderm
I believe Ian is correct. It's been a while but as I remember the BT length is used as part of the identifier to define which PLC transfer goes to which BT# in the PV. In any case, the length in the BT in the PLC must match the length as defined in the PV regardless of the amount of data you want to trnasfer.
Keith
Keith,
Use communication with Remote I/O.
Change the size in the plc is not an option, because the size of the data words for example 32 overwrite other data.
So I want change the size in the BT configuration.
The problem now is when I change example BT7 the size from 32 to 8 the group/slot value disappear and 2/0_ is not available any more.
Wat must I do?
mulderm
I have a Allen bradly pv1400.I have been trying ke to add 2 multistage indicators to the program. When i did add the indications and try to...
2,997
I tried to transfer a block to PLC,But got the message"block existing in eprom",i clicked yes and no,got "0 block transfered" I also tried to...
2,519
Hi, I'm trying to transfer all the blocks from a Siemens S5-115U CPU943 using Step5 programming software. The S5 is online and also it is...
11,559
I am using Codesys as my PLC Programmer. I use structured text as the language. I tried using a timer inside a function block and then mentioning...
1,581
I am getting ready to use an ArmorBlock I/O module for the first time. All I have done so far is connect power to it. When I apply power it goes...
2,661