ArmorBlock problem, first time user
Dec 2010
Burlington, NC
402
I am getting ready to use an ArmorBlock I/O module for the first time. All I have done so far is connect power to it. When I apply power it goes through the POST for about 10 seconds, the Net led flashes red once then the Module Status led flashes red. The user manual only says it is a recoverable fault, but it does not say what that fault may be.
Usually AB manuals have the answers but I couldn't find it this time.
Any thoughts?
The recoverable fault is most likely caused by the lack of a network connection. Once you have it configured and connected to the network, the fault should clear.
What exact part number is it ?
Have you connected it to a network ?
Is it an output module with an auxiliary output circuit that you have not yet connected ?
Is it an input module with open-wire detection enabled by default ?
If it's connected to a network and the Net LED is not flashing green, then there's probably something wrong with the network cable. My recollection is that a duplicate node fault gives you a steady red network status LED.
From the AB-1732E-16CFG manual:
MODULE status indicator MOD:
flashing red > minor fault
- firmware update
- IP-address switches have changed
- check configuration and cycle power
- if firmware-update , wait untill complete
- verify IP-address swiches are set to desired value
It is the 1732E-IB16M12R.
I have not connected it to a network yet, so maybe that is why. But I connected power to a 1732E-IF4M12R and its module light turns green. I tried connecting my network cable to it and it is not responding to it so I may have a network cable problem as well.
I will update when I have an answer.
Yep, it was my network cable. I am using the field installed M12 connector, and one of the wires got crossed.
I just wish the installation manual was a little more detailed about the led lights.
Thanks guys
Hello all, I have a 1732ES-IB16 Series A block that I have set the IP address on. I am unable to disable bootp using any method. I have tried...
346
Hello, I am stuck on trying to get an ArmorBlock, 1732E-16CFGM12QCR to respond to EIP outputs. My PLC is Panasonic FP0H-C32ET. I Registered the...
138
I am having trouble accessing the embedded web server of my 1732E-IF4M12R module. My digital modules accept the password fine, but the analog...
1,617
ArmorBlock 2-Port EtherNet/IP Module I am working on starting a plant up and we have a tremendous amount of these modules as the plant was...
2,532
Is there a armorblock type of that includes digital and analog I/O? All I can find is Digital.
1,433