When I plug FM350-1 module to rack with S7-300 CPU315-2DP the SF light is turn on at the module. The CPU315-2DP become error (SF light turn on). My hardware configuration is correct. Anyone can help with this problem?
Ali
Siemens Support
Try the above link and search for the FM350-1, there is a quick start guide, manual and downloads for configuring the FM350-1.
SF are caused by incorect configurations or software settings.
If you are still having problems post your set-up and I will try to help. I have just finished a project with 2 FM350-2 cards fitted and they are similar to a 350-1
Have you checked the wirings. (24V supply to 1L+ and 1M etc....)
Is the coding connector on the side of the FM350-1 set up correcly for the encoder(A=5V D=24V).
You can find more from the manual:
FM350-1 manual
BR,
TS
I have checked everything but still error. When i use online hardware configuration this message is shown in the module information :
Module configured, but not available
Preset/Actual mismatch:
(inserted and configured module types are not the same)
- Expected type: Counter module (6ES7 350-1AH02-0AE0)
- Current type: Not available
Anyone knows what does it mean?
Ali
Check the expansion bus connector behind the FM350-1.
If the connection is not ok then PLC can't "see" the module.
BR,
TS
Ali
When you install the FM350-1 package, the example programm zEn23_01_FMx50-1 is install at the Examples directory. There you can find an example of the programm that the FM needs.
Propably the SF Led is on because you haven't made any programm for the FM and it needs FC2 (CNT_CTL1)
Does anybody have any experience with the ouputs on the module.
I want the moddule to set the ouput when below comparison value 1 and reset when countervalue is above value 1.
In de HW-configuration I can set all this the only problem is that is doesn't work.
If anybody ever did this or knows how to do this please help me then
Right module inserted
Silly question,
hav you inserted the right module in your hardware configuration, that is typically your message if this is incorrect, otherwise the connection to the module must be checked.
Make sure you have the correct module no of card inserted , there are various types.
Regards
Rheinhardt
It is the right module with the correct nr.
The module does count and i can toggle the output manual.
But the module itself does nothing with the output when it reaches the the requested value.
Fm350-1
Hi, my name Tran. i research about FM350-1 but i can't do as i want.
can you teach me about this function.^^ or can you give me some project about this.
thanks for all ^_^
have you insert in OB100 the start address area pointer of the counter as image below. This in an example consider the FM350 having an starting address in hardware setup = 512
Here the linkweb to FM350-1 user guide setup http://support.automation.siemens.c...lib.csFetch&nodeid=1136199&forcedownload=truehttp://img801.imageshack.us/img801/7945/immaginezf.png
MODERATOR REQUEST:
If you have a new question, please create a new Thread for that question.
Go back one level in the Forum to the "LIVE PLC Questions & Answers" page, and use the Start a New Thread button.
If your question is directly related to an old question, you can link to the old question by copy/pasting the URL of the old thread into your new thread.
Can you please post the diagnostic messages your are getting on your CPU. You can access this by pressing ctrl-D when you have the project selected.
Moderator Request, part 2:
Please do not post responses to this thread. If the new poster who has resurrected the old thread creates a new one, he or she may proceed, but I don't want to continue this one.
I don't have the ability to "lock" a thread from future comments, but I do have the ability to delete posts, as well as to provide gentle persuasion.
It's part of a new volunteer Moderator-led campaign against "Zombie Threads".
We are currently encountering configuration problem with FM350-2 used for counting and totalizing functions. When we configure the FM350-2 and...
3,189
hi, I have a problem with module Modbus 6ES7 138-4DF11-0AB0 and module Counter 6ES7 138-4 DA03-0AB0 C. May i use these module together with one...
4,353
Hello everyone, I'm having issues with connected components. I got a new laptop and I installed all the RA programs I need without problem. I was...
335
I have a square wave being put into the Micro850 input channel 0. I have tried with counting the rising edges with code and with trying the high...
1,923
Hi everybody, I would like to start by letting you know that i'm a begginer in PLC programming and i can use a little help here, please. I'm...
1,590