problem with program for concrete plant with Omron CQM1H CPU 51
dikobraz9
Oct 2010
Drniš
Hello all of you!!! I have problem with program for concrete plant(CQM1H CPU 51,ID212 x1,OC222 x2,OC224 x1,AD042 x2) and need help from you.
Before reconstruction concrete plant have extractor belt for weighing and transport agregates to skip-agregate transporter to mixer- (4 agregates separately dossage on weighing system on extractor belt - 4 cells ),and after emptied belt,belt stop, skip go up to mixer.
When skip go up, agregate dossage go on to belt and waiting for skip to go down etc.
Old automation with CQM1H CPU51 suport these system.
Now, after reconstruction we removimg belt and put 4 cells on skip and agregate dossage go directly to skip weighing system.
Here is the problem- agregates,cement ,water and aditives dosing corectly- but skip wouldn't go up.
We tried to do changes on program but nothing.
I send you images pieces of old program and maybe you can help me, and if you want contact me on PM and I can sand you all program.
input signal when belt start after dossage
input signal skip down (limit switch)
input skip waiting (limit switch)-stop skip before mixser finish mixing
input signal skip hight limit switch(emptied agregate to mixer)
skip UP output
skip DOWN output
belt output (when finish agregate dossage)
conditions for skip up and down
Please help me!!!
THANKS ALL OF YOU!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!
It is almost impossible to help Without knowing what changes you have made.
You need to go online and monitor the program to see what is stopping it from working as expected.
Thanks moggie... Every changes which I made doesnt work, and I back program to previous state. In images you can see program without changes like in PLC. Can you help me with this? Thanks again!!!!!!!
Remove I0.02, and HR5.14 & HR5.15 put under I0.04(skip base limit switch),also change coil polarisation(HR5.14 closed,HR 5.15 open).After remove 101.04 (belt output) with 101.06 (skip up) with conditions from images. After that in automatic production dossage components are correctly but skip go up for a second and stop. If I force output 101.06 (skip up)automaticaly turn on 101.07 (skip down). Thanks....
So if the skip started to move up and then stopped; check online and see what is stopping output 101.06 from turning on.
I suspect it is HR5.15
Hi dears I am facing problem during program upload on S7 200 (226 cpu)microwin 4 sp9 closes on 100% I try to upload data blocks, its ok, System...
2,457
Hello everyone. I'm trying to write a program in ST which would toggle a bit with one button. So when the button is pushed the bool sets to 1 and...
3,666
Hi all, I'm hardly a Siemens expert, and am struggling with a conversion I'm working on right now. A system was purchased at auction, and I'm...
1,866
Hello, I am trying to find one varible used on my HMI in FX2N program...it is variable D726 and cross refference always direct me to line where...
1,367
Hi All, I need your help that i want to upload the program from Logix5572. Communication is OK through rslinx over ethernet. but when i try to...
3,567