Profibus topology with et200
dbozic
Oct 2013
Zagreb
74
I don't have many experience with ET200S with CPU capabilities so if someone can help with configuration. As I have seen the IM151-7 cpu is a slave. Network topology would consist of 2 field profibus transmitters, a siemens HMI panel and a IM151-7 cpu (et200s cpu). Do I need an additional master module for IM151-7 cpu for this to work and exchange data so that the IM151-7 is the master in the network or is this module unnecessary for this configuration? Sorry if it is basic question but I have never used et200 cpus as the only cpus in the network (I always used s7-300 as masters..)
The 2 field profibus transmitters I assume are Profibus slaves, therefore you would need the Profibus-DP Master module.
(http://support.industry.siemens.com/cs/products/6es7138-4ha00-0ab0/dp-master-interface-for-et200s-cpu?pid=241638&mlfb=6ES7138-4HA00-0AB0&mfn=ps&lc=en-WW
The master module would not be required for the HMI communication, and you could even keep that on the built-in Profibus port, separated from the network with the transmitters.
Thanks alot! I also understood it like that from the manuals but I needed some reassurance. Thanks for that! Yes, transmitters are slaves so I will need the master module.
Hi, I'm working on a project right now where my client has an existing GE RX3i redundant PLC system, with Profinet communication cards in the...
3,920
Hi all, Is it possible with cx-configurator to upload the profibus network with the slave address mapping? I tried but failed with a CJ1W CPU22...
3,835
Hi, All the TimeOut shown on the graph of profibus scan are related to Diagnostic repater. Should it be the case? or is there any problem? NB...
1,675
Hi Guys, CPU: S7 414-DP, Siemens. How to get Profibus Topology? In HW config and Netpro I can see what devices are connected to the profibus...
3,820
Hi, I was noticing that Profibus connectors have 2 ports on them that can house 2 separate cables. Can I use 2 cables with Profibus signals...
186