I am using an Emerson CPL410 cpu as a PROFINET master. I don't believe that this CPU supports PROFIsafe, as otherwise it would have been mentioned all over the documentation (however I may be wrong about that)
One of the devices on my PROFINET network is a safety rated Huebner Unit One overspeed switch (UO-SCU-G), (and this next bit is a bit confusing to me) that is supposed to be interfaced to PROFINET via a UO-EPN-2 (which is apparently the non-PROFIsafe interface, I believe that the PROFIsafe one is UO-SPN-1)
The only GSD file that I can find for the this system ("GSDML--V2.3-HU-024A-AMPN(H)41-20150424") includes a fixed set of modules when you create an AMPN(H)41 device on the network. These modules are (leaving out slot 0):
While the "non-safety" slot only has
My questions are:
Previously I have only used U-Ones on PROFIBUS, and I had a lot more confidence in the way the system worked.
Finally I am not in control of hardware design, and that is happening on the other side of the planet anyway. I'm just trying understand what is being asked of me.
One of the devices on my PROFINET network is a safety rated Huebner Unit One overspeed switch (UO-SCU-G), (and this next bit is a bit confusing to me) that is supposed to be interfaced to PROFINET via a UO-EPN-2 (which is apparently the non-PROFIsafe interface, I believe that the PROFIsafe one is UO-SPN-1)
The only GSD file that I can find for the this system ("GSDML--V2.3-HU-024A-AMPN(H)41-20150424") includes a fixed set of modules when you create an AMPN(H)41 device on the network. These modules are (leaving out slot 0):
- Slot 1 AMPN(H)41 I/O Safety
- Slot 2 AMPN(H)41 I/O
- PS input cam
- PS input status
- PS input velocity
- PS output control1
- PS output control2
- PS output preset multi turn value
While the "non-safety" slot only has
- input cam
- input velocity
My questions are:
- How well is this mishmash of PROFIsafe and non-PROFIsafe components going to work?
- Should there be a GSD file somewhere that matches the non-safe UO-EPN-2?
- Is it likely that the inputs marked "PS" will also get populated along with the non-PS inputs?
- Is it likely that the "PS" preset can be sent across a non-PROFIsafe network to the device?
Previously I have only used U-Ones on PROFIBUS, and I had a lot more confidence in the way the system worked.
Finally I am not in control of hardware design, and that is happening on the other side of the planet anyway. I'm just trying understand what is being asked of me.