program after plc shut off
Yes and No!
It is possible to compare two different time.
When the PLC shuts off you can move the RTC(Real Time Clock) value to an holding register array and later compare the new actual value of this RTC to the on you memorized earlyer...
Hence you will have a time duration value which will still take into account the time when the PLC was OFF...
Besides that, OFFF really means OFF
programm after off
wow! that was quick. The (Off) i mentioned is really off. THe power supply to the plc is off. THere's no supply to the plc. You see, the plc is located inside the machine, and our customers tend to shut down the supply to the machine, and well everything restarts when the machine is powered on again.
Omron CPM1A (AC).
If your using a CPM1A, try using counters as timers. Counters are retentive and retain their current value on power down.
Example:
If you were using Timer 000:
Timer Input 0.1 sec clock
00.00 255.00
|---| |-----| |--------------[ CNT ]--|
| [ 000 ] |
| Reset [#0100] |
Use contact of CNT 000 instead of TIM 000 as output of timer.
This makes an accumulating timer rather than one that loses its current value on power down. It will pick up where it left off when the power down came.
It will not continue to time with the power off, but maybe you could do math like Pierre suggests to move the differnce to the current value.
programm after off
thanx alot guys, the cnt worked! But the cnt value seemed to be interfeered by one of the (ADD Function). I placed a 0.02sec pulse infront of the (add) which i use to represent an encoder. THe value disturbs the CNT VALUE.
Did you leading edge condition (one shot) the Add function? If not your counter value is going to go wild. Use an @ in front of the ADD (like @ADD) to differentiate the ADD function.
program
I guess i'm too weak. Well, yes i have all the math fuction already set in LEADING EDGE from the beginning. But perhaps something else is wrong, I cant find the cause. The CNT value isn't counting. perhaps you should look at the diagram.???if it's no trouble to you. How to save as jpg?
Reading on this older stuff I remembered that when you pick a counter or timer number in those OMRONs PLC, you have to be carefull...
Timer # 1 ... T001 has the same memory allocation as counter # 1 CNT001.
If you have a T001 ...AND... a CNT001, they will interfere with each other.:cool:
One trick is to pick your counter number before you write the program... say you'll be using 001 to 030 for copuntersand the rest for timers... it prevents those funny things like changing values...
Pierre makes a good point. Another way of avoiding this conflict would be to always start with timer #000 and counter #127 (or whatever the highest number is). Then, as you need more timers, use 001, 002, 003, on up. As you need more counters, use 126, 125, 124, on down. This avoids having to allocate a specific number of timers or counters beforehand.
Back when I last used Omron stuff, we were limited to only 48 timers and counters (C20s era), so you had to use them sparingly!
-Eric
Yes! Yes!
Many thanks! The apllication worked just the way I wanted it to. It's the first batch of our machines using PLC. We were using HARDWIRES previously! You should've looked at the reaction on my superiors face when the machine came to life.
it depends r u refering to retentive memory a timer will retain its values when power to processor is lost but if the counter or timer is a progammed function meaning executed solely by the cpu then when power is lost all counting or timing will stop.
Can we use a Simotion D455 ethernet port x127 as a gate, to access S7-1500 plc Tia Portal program ? In the Simatic manager, we used Netpro to do...
87
Posted this to Reddit with little success, so I figured I would share it here as well. Very new to PLCs, but figured I would give it a shot to...
123
I'm a beginner in the automation field and I've set up an automation system connecting several devices (datalogger, radio, etc.) via Modbus RS485...
215
Hi All, want to ask. I have PLC a programme to control the valve. The existing programme is to control valve A (Y22), and I want to change to...
145
can anyone has a good program to learn plc programming online. i have the basic looking into improve my skills thanks
145