Program memory, Ksteps, bytes - Omron
Boyko
Oct 2005
26
Hi.
In the Omron CJ1 CPU11 manual I can read that the program space is 5 Ksteps. What does that mean. How can I understand how many Ksteps my program is?
When I transfer one of my programs to the PLC I get a message for 10600 bytes transfered. I can conclude that one step is not equal to one byte.
Boyko
Page number 375 in manual W393 explains the "User Memory" (UM)
You actualy get a small amount more than your 5K in that plc. (6140) This memory quanity is how many steps you can have it your program (for that processor). One step equal one word.
10 contacts in series with one output would consume 10 steps.
A network with one contact before the Xfer function(function 70), would use 5 units of memory.
Page 375 is the start of the table that lists each function/intruction, and how fast it scans, and how much UM it needs.
CXP will show you how much of your memory you have used, goto "View", than "Memory View".
Hope this helps
Hello friends, long time lurker first time poster here. I have a, lets say, unique situation with a CompactLogix PLC where we've lost the program...
370
Is there anyway to be certain that the memory module in a ML1400 has been written to with the current program? I have controllers in the field...
872
Hi All, I have an Omron PLC program which is copied from the memory card. Could you please tell can I open the PLC program using CX programmer or...
960
In the Allen Bradley alternate reality program logic and program data are linked together. Is it possible to update a Micro Logix program with out...
4,473
I have a product that uses a Siemens Simatic s7-1200 PLC. My company did not write the PLC program, but we have the program on an SD card. We...
2,265