PROGRAMMING WITH CodeSys
ebotsmith
May 2012
Eindhoven
I am programming an Automatic Car Washing System in CodeSys, I am using SFC and Ladder diagram. I am having an error in my program which states:
Error(4355)A transition may not have side effects
I will appreciate if someone can help me with a clue on how to tackle this problem
Thanks in advance
Don't assign the logic to your transitions. They're simple enough to replace them with in-line ST. For example, replace the transition CarDetected with Sensor_Detect_Car or Sensor_Detect_Car = TRUE (whichever is more readable for you).
Good Luck!
(8{)} :) .)
(Yosi)
sidney you found me,
yosi in sidney worksheet they must use ladder in the transitions (as this is a requirement for IEC
Have you tackled the problem?
In the help documents of CoDeSys v3.5,​
CODESYS Development System > Reference, Programming > Programming Languages and their Editors > . Sequential Function Chart (SFC) > Elements > SFC Elements 'Step' and 'Transition'
As opposed to CoDeSys V2.3, now CODESYS treats a transition condition like a method call. The entry has the following syntax:
<transition name>:=<transition condition>
(for example trans1:= a=100)
or only
(for example a=100)
You will find an example (condition_xy) in the figure above.
In the help documents of CoDeSys v2.3,​
Transition / Transition condition
A transition condition must have the value TRUE or FALSE. Thus it can consist of either a boolean variable, a boolean address or a boolean constant. It can also contain a series of instructions having a boolean result, either in ST syntax (e.g. (i<= 100) AND b) or in any language desired (see 'Extras' 'Zoom Action/Transition'). But a transition may not contain programs, function blocks or assignments!
Your program can successfully run on CoDeSys v3.5 with some small changes. Read the document Comparison_CODESYS_V2_to_V3.PDF from the official website.
Does anyone have any experience of using an ***** Flexy for remote programming/maintenance of a Codesys based controller? Rather than using the...
234
hello all. i need help to connect my Beckhoff PLC with the codesys. i have tried the codesys RTE tool but i coudnt connect to the plc. can any...
3,869
Hi, Where I can get Codesys V3.5 on IEC 6-1131-3 PLC Programming Training in India. Thanks & Regards, Anklesh
2,409
I am looking at the new Altivar61 VSD from Telemecanique with "controller inside" the programming is done using CoDeSys. I have downloaded the...
3,844
122