although you can use these terminals, they are specifically designed for supply voltage and not analogue control.
please pst the link to the site so I can look further
I agree with Iant. I only use this type of terminals for the control supply voltage (GTF76/230 from Phoenix contact).
For the 4-20mA analog inputs and outputs, I always use the normal disconnect terminals, so I can measure the loop current without opening the circuit.