Gil47
Member
Thank you very much for your help. So we are out of compliance with the NEC and could be causing a potential problem of a fuse not popping or breaker not tripping? Or someone getting shocked because we have opened a grounding path? I just want some ammo to argue this with upper management to make them do the correct thing or at least let them know the dangers involved. We are using a grounded neutral on our transformers and all our cabinets are earth grounded.
Thank you very much for your help.
Maintenance Man, I feel you are on the right track,
here is a problem I see,
If the wire Nuetral from the NC on the overload and the coil gets shorted to earth then the overload contact position NC or NO will make no difference as the contactor coil will stay pulled in, now if you used the live supply then a short between the overload NC contact and the contactor coil would blow a fuse.
I believe that outside of the America's the opening of the Neutral would be against the code.