PTO Function ML1200

alphav

Supporting Member
Join Date
Sep 2007
Location
Ontario
Posts
35
Hello, I have problem using the PTO function. When Use the Frequency output function MOV 2000 PTO:0.OF I have no problem, but when I try to use the Jog Continuous function
MOV 1 PTO:0.JC I get the error "Address must be specifyed to
word level!" I can not see what I am doing wrong. Any ideas?

thanks,
gerry
 
I guess you have to move to the JF (Jog Frequency - Hz) element, not JC, which is just a bit to control the Jog output...

The PTO JC (Jog Continuous) bit instructs the PTO sub-system to generate continuous pulses. The frequency generated is defined by the Jog
Frequency parameter in the PTO function file.


See the Reference Manual, page 165.

- fuzzy logic
 
Sir i have a doubt.. I have MLX 1400 (BXBA) ...I connected +24 VDC to VDC1(group2) and by default i am getting +22VDC in output 2,3,4(group2, FET outputs) even when i am not switching ON the output.... Is there any problem in PLC
 

Similar Topics

Dear all, Pls help to generate PTO in AB 1400. And also how to do wiring for pulse output in group 2(output 2,3,4)
Replies
9
Views
8,779
Hi, I have a Micrologix 1500bxb set up to run a servo for a press feeder. Basically, a limit switch(XIO)on the press causes the rung which the...
Replies
4
Views
3,725
am planning to build a small machine which have 2 Axis (linear motion and rotary motion) am confused about using closed loop stepper motors (PTO...
Replies
0
Views
1,016
Hi Everyone am controlling a stepper motor with 1215 plc, when using motion control(V6/7) you don't have any option of using HSC as feedback is...
Replies
0
Views
914
Micrologix 1400 PTO function file. I set ADI to “1”. Right clicked ADP, selected “set independent accel/decel value location”, and entered L9:0...
Replies
0
Views
791
Back
Top Bottom