I assume that I have to deal with centrifugal Pumps... They are 22kW each and are used to spray liquid on products.
So, when I lower from 50 to 40Hz, then we lower 20%.
51,2% Input Power needed if I calculate it with the formulas I've seen in previous posts ((40/50)³). The flow and pressure remains pretty good If i look in these curves.
Is this all right ?