PV550 Communication Problem
alphav
Supporting Member
Sep 2007
Ontario
35
Hello All,
I installed a system with a PV550 and a ML1500 with two 1761-NET-AIC's a couple of years ago. The costumer want to do some changes to the HMI, so I am trying to modifye the HMI in the office using an old PV550 (2711-B5A5 FRN 1.07) and a ML1200. I did it 2 years ago but now I can't.
I am conecting my laptop to one of the NET-AIC's via an 1747-UIC and cable 1761-CBL-PM02. and the micrologix to the other NET-AIC with cable 1761-CBL-HM02. This works fine, I can see the Micrologix 1200 in RSLinx.
To connect to the PV550 I am using cable 1747-CP3 with a NULL-Modem adaptor.
If I connect the PV550 to the NET-AIC where the 1747-UIC(laptop) is connected to I can see the PV550 in RSLinx but not the ML1200, and the same time the PV550 shows the error message "Require network node(s).
If I connect the PV550 to the NET-AIC where the Micrologix 1200 is connected to I can't see either the PV550 or Micrologix 1200 in RSLinx but I do not get the "Node" error message on the PV550.
Instead of using cable 1747-CP3 with a Null-Modem adapter I also tryed to use cable 2706-NC13 (straight trugh cable) as I think I did 2 years ago, but that doesn't work either.
Any Suggestions
Regards
gert
See pic below
Baud rates must be the same each node must have a different node address. ML1200's port must be configured for DH485.
Power to both AIC's?
Thanks for the reply (again)
I did exactly as in your diagram, using the 2711-NC21 cable. ( I am using an 1747-UIC between my laptop and the 1747-CP3 cable going into the first 1761-NET-AIC) ---- Still not working. Then I made an adapter between the 2711-NC21 cable and the PV550 where I tryed the following a) Disconnected pin 8, and b) crossed pin 7 & 8. Either way I can see the two devices in RSLinx, but I can not download a program to the PV550.
Getting "[Error 2258 - Unable to communicate with operator terminal, did not receive a response.]"
Laptop = Node 0
Micrologix 1200 is set to Node 1, Baud 19200
PV550 is set to Node 2, Baud 19200
Regards, gert
Thanks Mickey
When I opened up the link you sent, I imidiatly recognized the frace DO NOT USE AUTO CONFIGURE! The "1770-KF3/1747-KE" configuration, was what I used 2 years ago.
Connecting the 1747-UIC and the PV550 with the 2711-NC21 cable to one NET-AIC works fine. I can see the PV550 in RSLinx and I can download as well.
However, if I connect the second NET-AIC and connect the ML1200 to that unit, the network stops working. To solve that problem I made an adapter going into the PV550 with pin 7 & 8 crossed, then everything works.
Thanks again....
gert
Well glad to hear you got it working.
But I'm confused as to what/why you did with pins 7 & 8. Maybe a drawing of this would help.
See below a drawing of the 2711-NC21 cable
I bet someone has already posted the answer to this , but I haven't found it yet: I'm helping out a friend who has a PV 550 (2711-K5A2)...
3,003
I have a Panelview 550 and I need to access the program and download it. At some point the back cover of the case must have broken off and I...
2,349
Hello I need some help, i have a pv550 that every other day give me a 637 fault: communication driver fault, every time I recycled the power the...
2,250
Hello! Communication setup of the PV550(2711-K5A8) under configuration mode looks like: DH+/node2/Br57.6 I use 1747-UIC interface, 2711-NC13...
2,112
Hello Good Day, I would like to find out how to configure comms between PC (panelview or RS Linx) and PV550 touch.🔨
2,850