Ok. I've done some testing with a spare refurbished and blank DH-485 PV550 terminal. We have a few still in service here so I have to communicate with these terminals a few times a year.
You have...
PanelView 550 2711-B5A2 FRN 1.04
1747-UIC and Ethernet patch cable (don't have a NC13)
RSLinx Classic v2.59
Windows 7 64-bit
I have...
PanelView 550 2711-K5A2 Series F FRN 4.48
1747-UIC SER A REV D FRN 1.03 and Ethernet patch cable (to match your setup)
RSLinx Classic v2.59
Windows 7 64-bit
You have...
RS-232 DF1 Devices driver...
Comm Port: 4
Device: 1770-KF3/1747-KE
Baud Rate: 19200
Parity: None
Stop Bits:1
Station Number (Decimal): 00
Error Checking: CRC
Protocol: Full Duplex
I have...
RS-232 DF1 Devices driver...
Comm Port: 8
Device: 1770-KF3/1747-KE
Baud Rate: 19200
Parity: None
Stop Bits:1
Station Number (Decimal): 00
Error Checking: CRC
Protocol: Full Duplex
I powered up the terminal and checked that it has the default communications settings...
• Max Node Address = 31
• Node Address = 2
• Communication Rate = 19200
With my RS-232 DF1 Devices driver running with no PORT CONFLICT, I connected the Ethernet lead to the PV550 and it showed up in the RSWho session within seconds.
I would always advise users to stay clear of Com Ports 1 - 4 for the 1747-UIC. Windows tends to share resources between 1 & 3 and 2 & 4. I use 8 as a default, but 12 or 16 should be fine if they are not in use.
Did you check that Ethernet lead is OK?
Had you connected an Ethernet crossover lead by mistake at any point prior?
Is the UIC able to communicate with anything else out the RS-485 port?
Silly question, but is the switch on the UIC in the correct position?
The older FRN 1.04 on your terminal is sticking out at me as well, but I don't think that would be the issue?
Another thing to try is to flush the Harmony cache files for the drivers in RSLinx Classic...
48241 - RSLinx Classic: Clearing cache by deleting Harmony files
Access Level: Everyone
Regards,
George