Quantum RS232 to Multilin via DIO
Feb 2016
Alberta
Alright, here's the issue. We have a local rack connected via DIO to a second rack not far away. In that DIO rack we have a NOM card that is connected*to a Modbus Bridge/Mux.*
Local Rack(NOM Card)---->DIO Rack (CRA Card)----->DIO Rack (NOM Card)-----> Modicon Modbus Bridge/Mux (NW-BM85C002)------> Out port #3 Modbus RTU 232 to a 485 converter and then to the 485 Port on the Multilin 369.*
Is this even a supported configuration? We have it all installed and wired and can't seem to get any communication.*
If it is supported, what am I missing!? Routing tables in the Mux? PLC is a master and the Multilin is a single non networked slave.*
Thanks all.*
I would start with the most basic and get a computer talking to the multilin through the 232-485 converter. then you will know you have baud 8N1 etc correct.
Inevitably RS485 doesn't work the first time so I also to swap the wires on RS485 connections every time I change another parameter.
I managed to get it working! After quite a bit of research I had to do the following:
- Hyperterminal to the Mux to set the port settings of the port I wanted to use.*
- Set up MSTR instruction to essentially look out the slot of the NOM card (local rack) and point to the Modbus plus address of 31 (the mux) and specify which port of the mux.*
The rest fell into place.*
hi All Can you please help me to find the right software to open Zip backup of 434 12A PLC? Any major steps I need to know when opening? Regards
18
Hello All, Was hoping I could get a little help with Modicon ladder logic. This is the first time I have seen Modicon logic and currently trying...
278
Hi There, I have a Modicon Quantum PLC, there is a alarm on display "noConfig" its happened after power failure, I have gone through manuals...
658
Hey guys. Mostly new to this stuff so I apologize if I'm not following proper format. I have 3 working CPU133 /3s. There is a desktop with a...
901
When i read the specification of 140CPU43412A i observe that as remembered in specification 1. Local i/o : Maximum i/p and o/p words are 64 in...
501