Quick Question on PLC Ladder Logic Execution
mike64b
Oct 2011
richland
77
I've got a AB Micrologix 1200 PLC and I've attached a picture below showing a rung with a nest. If B3:2/5 is initially cleared and we go to SBR U:7 and within that SBR I set B3:2/5, when it returns, will the JMP Q2:1 be executed next or skipped because it would re-evaluate the entire rung?
I just tried it on a ML1500. I used a OTL ( output Latch) instead of a JMP instruction and it executed. The OTL latched.
Mickey thanks so much for taking the time to check it out. I was worried that upon returning to the rung it would first re-evaluate the B3:2/5 XIO and if that was true do the JMP, but it seems it actually operates as I hoped!
Considering you tested this out, does that imply this rung example is not common? I hope I am not attempting things that are considered in the dark realm of ladder logic :)
If you ever have any doubt about how a rung will execute then double click on the rung number. The mnemonic instructions for the rung will appear. The rung will execute the instructions in exactly the order listed on the mnemonic line.
I would have suggested exactly the same thing Alaric. Nice tip.
Anyone who has ever been on a Rockwell training course will have course material with diagrams that show the RET from a subroutine returning execution to the start of the next rung!
That is WRONG !! Execution continues from the right-hand side of the JSR, and if the next instruction is NXB, execution continues on the next branch down.
This makes sense to me... I'm glad it operates in this way as when I do a JSR I want it to return to exactly after that JSR and not do anything funny like re-run the rung.
Complete sense is made if you treat EVERY instruction as just "an instruction" - it doesn't matter what instruction it is, the remainder of the rung will be processed as normal.....
... an exception - JMP will jump to the specified label as it is encountered, no further processing will be performed on the rung.
See the pic to understand this - there is no other reason why any_tag should not be true
Yep I see what you are saying, this operation follows what I would expect since I am used to C type and assembly language programming mostly. Ladder logic is very new to me.
Edit: Another quick question.. Any reason why labels cant just be a rung on there own without an output? Is it just do to the fact all rungs must have outputs? And can a workaround just be, for the rung with a label, to latch some internal bit that is never used?
In a ControlLogix processor you can use the NOP instruction (no operation) as Daba showed. Otherwise all rungs have to terminate with an output instruction. In your Micrologix you'll need to have a work around. One good one is just what you suggested, an OTE or OTU assigned an internal bit that isn't used. However there is not any reason that you can't just proceed with whatever logic is on the next rung right after the LBL on the same rung as your work around.
Note that also in your Micrologix you can't do what Daba showed with the JMP instruction. In the Micrologix case the OTE any_tag would be required on a branch below the JMP instruction. Despite that it would be jumped and not executed as Daba explained, leaving any_tag in its last state.
Should have replied in MicroLogix context - apologies :oops:
Well now that I think about it, I am usually using the JMP to go to the end of an SBR and in that case I would just have the output condition as a RET on the label rung so thats not an issue.
That leaves the only issue in the main program LAD2 where if I want to jump to the end I wouldn't have anything on the output... I wonder is this an area where instead of using a JMP I would use TND to perform the I/O scan and restart the ladder scan from beginning?
TND just acts like the end of program file, its like the processor sees the END rung. It is not normal to use a TND in the main program file, TND is a debugging tool, and shouldn't exist in a finished program.
In a subroutine, I would program an "early return" = a conditional RET instruction if I didn't need to process any more code.
In the main routine, LAD2, I would NEVER EVER program anything to stop the rest of the code executing. Doing so makes any code added "position dependant".
It sounds like you are trying to tie your logic execution to the application - let the logic solve whatever is thrown at it.
If you want to conditionally end a subroutine early then use the RET (return) instruction. Use with care and structure your subroutine carefully because any bits addressed by any OTE instructions after the RETurn will be left in their last state.
check back on my previous post - i was editing while these later ones came in
I apologize for not having the model of the plc. I am trying to get it. I have a print out of the program and it seems straight fwd. One...
3,436
What is the current cable to use to connect a laptop PC to a PLC-5 channel 0 (25 pin connector). I have a homemade cable that is just like...
1,537
I have a solenoid powered off a 1756-OA16I. The output has a fuse and then runs off to the solenoid. Now I am not able to change the card at...
1,433
Hi everybody i am currently working with a project at my company and i have spent mostly of the evening yesterday and the morning today trying to...
4,017
E
I am new in the field so bare with me please. I just programmed this PLC controlling this machine. I want to test my process to see if it works...
38
12,189