QX451 to WAGO Field Bus Coupler
FarHeap
Feb 2014
Nebraska
Here's the basic system in question:
WAGO Modules, in physical order;
750-352/020 : ECO Field Bus Coupler
750-530 : 8 Channel Digital Output
750-602 : Power Bus
750-602 : Power Bus
750-602 : Power Bus
750-600 : End Module
These are connected to a Horner, QX451 touchscreen PLC via Ethernet MODBUS TCP/IP.
This is a completed working system at this time. Everything is configured, and functional, with the existing modules mentioned above - the coupler has an IP address assigned, etc.
I need to add two new 750-554, Analog Output modules.
My questioning is as follows...
Do I need any special software to set up the WAGO modules, or can I just tack them to the end of the other modules, (before the End Module)?
Then, can I just assign tags in programming for the new WAGO I/O process image based upon the location of the new modules?
Will the addition of the new modules change the address locations of the existing modules' points?
I have not yet worked with WAGO equipment, so any help is appreciated.
Thanks.
Yes it does change the addressnumbers
each module has two outputs (thus 2 words)
The sequence is not important where you put them, you started with %QX0.0 that will become %QX4.0
and the analog outputs will satrt with %QW0, %QW1,%QW2 and QW3.
they do need power bus, but you have an unused one just before the 750-600.
analog is always first as this asks for complete words,
So in your program you will have to look for these outputs hopefully they are all declared in the global var list.
I've got a Horner Electric QX451 that I am setting up on a job. I will be using an HMI program connected to the QX to allow operator control...
4,623
Hello, I am in possession of a WAGO PFC 200 750-8216 which I was successfully able to set up as a Modbus RTU Master to a slave device using...
91
I have a project to setup base programs across multiple PLC platforms that can be used for Modbus communications to various sensors that have...
127
Hello, I m having a problem with wago 750-862 plc. The plc won't start automatically in run mode after a power reboot. I've also tried the...
373
Hello everyone, I am trying to setup a Wago 750-8100 PLC to send a text message out via ethernet port, if I get a Digital input that is true. I...
348