RA -Modbus TCP AOI - number of transactions
frandESS
Sep 2022
Norway
Dear Forumers
I'm developing an ESS project with Compact Logix L36ERM and using the MBTCP Client AOI from Rockwell.
I'm using 4 AOI blocks for one IP adress/client. FC's used is 1/3/15/16.
When running one instance, no failures occur.
When running more than 1 AOI block enabled i get series of strange socket errors and believe i overload (not wait enough time until next poll) Error is 16#00ff that is a close socket message.
How can timings and waiting time be managed?
Without a Wireshark trace, I suspect that your Modbus TCP Server device can’t handle multiple TCP connections. As a result you have only one AOI connected.
If you need more than 5 transactions, then you can simply change the Ref_trasactions array size, however this will slow down processing because all transactions processed sequentially and it takes more than one scan to process a transaction. You may need to increase the default poll to 2000 or even higher.
There is another way to manage transactions dynamically:
Once transaction is done, you disable it, put new addresses and FNs and then enable it again.
I also see that first and second AIOs are sharing the same Modbus Data array. Is this intentional?
Is there a chance that you did not use Rung Import process for all AOIs, and used Copy/Paste?
Can you post ACD? Or can you export these 4 rungs and post these here?
Dear Contr_Conn,
Thank you so much for your response.
You mention something that made me think, added a few more IP addresses in the slave device, same IP adresse since Slave can have up to 6 masters. (Its a ABB RTU540)
That solved it all, and also thank you big time for seeing my experimental mistake of dropping wrong tag on the data output.
I always import this AOI's
Anyways as you see, its kind of messy in writing FC15, i have to take them one by one instead of using a range - really dont know why its like that (checked in RTU and signals is declared as FC15) - taking them single is although working fine.
FC1 and FC3 is fine reading in bulk series.
3 screendumps attached
Again - big thanks
I have a PH meter that I am trying to bring its data into 1756-L81. I have downloaded the Rockwell MODBUS AOI kit, but I am not sure if I need to...
176
Hello, I am trying the AOI provided by Rockwell to read Modbus TCP, the version is 2.04 The connection looks good to the modbus server. I...
657
So I am working on a project and I am having problems trying to get this all to work. I had it working but lately I have been getting a fault on...
4,860
Good Afternoon , I have a project coming up for a labeler and a CompactLogix PLC . The communication for this labeler is Modbus / TCP ...
2,380
Hi all, I've been trying to get Modbus TCP to communicate (read only) with the Modbus TCP AOI that Rockwell provides, but I'm having issues and...
2,161