Ramp Rate Calculation
b104
May 2017
nova scotia
I have a winder that winds plastic to a certain length and i am trying to calculate the accumulation of plastic during a linear ramp down. Basically if I'm running at 500 feet per minute and ramp down to 0 feet per minute over 60 seconds how much plastic will accumulate on the roll after that 60 seconds is up? Is there a formula for this?
If you plot the velocity vs time, the distance traveled is the area between the velocity line and the time axis. In the case of a straight-line deceleration the area is one half of the starting speed multipled by the deceleration time, or in this case, 250 feet.
Steve's answer in equation form:
d = (V * t)/2
If you actually know acceleration instead of time then you can use:
d = V^2/(2 * a)
In both cases make sure all of your units are consistent. For example, you can't mix feet/minute for speed and seconds for time.
Keith
Hi Friends; I want to develop ramp function what function block i use to develop this in rs logix 5000? Image attached. I mean Linear curve how i...
4,263
Hello! Hope you are great. I need to make a change in a PLC with ladder logic. I will mount a analog valve and I need to control it in ramp up...
319
Hi hoping someone can assist me with current issue I am experiencing with an ABB drive. Problem I’m experiencing is a ABB drive supply a large...
210
Hello, I'm quite new with using FactoryTalk View Studio. I am currently using FactoryTalk View Studio 13.00 and creating a runtime file for an...
968
Hello PLCS Nation, I am hoping you can help a newbie find calculations on how to determine Line Ramp Up & Ramp down Speed. We have a machine...
1,194