Ramping Control
yulius
Guest
Y
Hai,
I am yulius from Indonesia.
I have a problem about ramping control.
Does everyone have know a program how to control output analog with used ramp control. Has a ramp up ( acceleration) and ramp down( deceleration)
rgd
Yulius
Ramping can be done fairly simply. If you are ramping a PID controlled heat zone, for example, you would simply take your slope (ie. 5ºC / 10 minutes)(the rate at which you want to heat), set a timer, and at the timer done, simply increase your setpoint, repeat untill final setpoint.