Hello Ken,
Today i observed that i made mistake in rotarty switch of S4, As i am using only one read head so rotaty switch S4 should be on postion 1 not on position zero , yes read head address should be zero is if using only one read head and EIG address should be 1.
Finally we changed the EIG S4 switch to 1 and test the same logic which you advice and i made and shared with you. And result is LED status of STATE is still blinking RED & Green. But now all the three MSG instruction for read and write now giving error message. Please find attached the image 10, 11 & 12 as attached.(Please see carefully error message on the MSG instruction on the attached images). Let us know what is the mean of these errors.
All other DIP switch wiring are correct like Read head Address is set to Zero baud rate is 62.5k terminating resistance on both read head as well as EIG module is ON. And RS485 wiring is as per manual. Now there is only one doubt EIG module baud rate setting for RS-485 is not giving in manual we assumed that it is fixed and 62.5 KBaud.
AKG
Today i observed that i made mistake in rotarty switch of S4, As i am using only one read head so rotaty switch S4 should be on postion 1 not on position zero , yes read head address should be zero is if using only one read head and EIG address should be 1.
Finally we changed the EIG S4 switch to 1 and test the same logic which you advice and i made and shared with you. And result is LED status of STATE is still blinking RED & Green. But now all the three MSG instruction for read and write now giving error message. Please find attached the image 10, 11 & 12 as attached.(Please see carefully error message on the MSG instruction on the attached images). Let us know what is the mean of these errors.
All other DIP switch wiring are correct like Read head Address is set to Zero baud rate is 62.5k terminating resistance on both read head as well as EIG module is ON. And RS485 wiring is as per manual. Now there is only one doubt EIG module baud rate setting for RS-485 is not giving in manual we assumed that it is fixed and 62.5 KBaud.
AKG