Reading RTD values...can anyone explain this?
Mas01
Oct 2020
Leicester, England
1,109
The values in blue are the live, monitored values and are all consistent with a cold day where our rig has.not been running for a while. So it looks like the integer values, you just divide them by 10 to get actual values.
Does each rung represent an individual channel on the card?
Can't understand why there's a need to subtract decimal value 6 or decimal 7 from the G-words(?). Mystery!
It seems that these K constants are an offset because the programmer believed that the read temperatures were between 5 and 8 tenths higher than the real ones.
Not exactly, the Ux\Gx are the (U) address (G) buffer memory and the K is the word number so in this case it is reading buffer memories 11-18 (assuming 8 channels) in other words the digital value of the A/D conversion this is obviously the Temperature probes and is in decimal format with an implied one decimal place so converting to a float then dividing by 10 will give you xx.x Deg C, often there is no need to convert to a float as it can be used for calculations as a decimal and many HMI's can use implied decimal places so 100 on the HMI will display as 10.0.
Edit: May seem confusing but what appears to be reading similar addresses is that there are a number of RAW digital values, these are direct conversion, filtered conversion etc.
There are other ways to read values from the buffer memory using the From instruction for example [FROM K11 K8 D10] but this fetches 8 words from address 11 to 18 and stores them in D10-D17 so only one call to fetch all 8 channels.
Thanks for this.
Question: how can you tell the K are word numbers and not decimal integers? From the code it looks like a subtraction command. I don't understand that.
U0\G11 to U0\G18 are 16 bit registers on the Anolog Input module that are transfered after integer subtraction to D11 to D18 that are PLC 16bit registers.
K constant is an integer decimal constant, H is an integer hexadecimal constant
To know the exact meaning of U0\Gn registers you need to consult the Analog Input module manual.
H? H doesn't come into this question.
Were you trying to reply to my other thread?
Oh Dear...... forget my last post It's my bad on this one, I was actually doing a bit of code for someone else at the time using the TO/FROM instructions & got my nickers in a twist, and of course probably with your other post. They are subtracting constants from the values in decimal, although it is only 0.5-0.8 Deg C.
The problem is I was thinking about the FROM instruction where two constants refer to the Buffer address & the number to fetch forgetting the Ux\Gx notation of using the buffers directly in the code.
Hi all, I'm looking at starting a project that would require me to use an RTD to monitor temperature in an enclosed environment. I'd be using an...
4,382
Hello all, I am fairly new to the PLC world and doing some self learning to pick up the nuances. Your help is highly appreciated. Question: I...
2,834
Hi everyone, As I am new to S7-300. i configured S7-315-2DP with 2 input card & 1 output card..with AI8 RTD module in which 6 i/p's are used and...
1,956
I am working on Control logix processor L 1762 & 1734 IR2 point IO Module I want the programming procedure or sample program to read the RTD...
2,327
1,738